vaporstat or no
Paul_87
Member Posts: 37
I just replaced a boiler on a Trane vapor system. I installed a vaporstat but it was defective. I put the pressuretrol on because I have to order a new vaporstat because no one has one in stock. It seems to run a lot longer cycles with the pressuretrol than the vaporstat. It kept short cycling with the vaporstat. I definantly need more venting but even when I removed the vent it would short cycle. I have plenty of B dimension 45". What would happen if I left the pressuretrol on and didn't use the vaporstat. The system was running at 1 pound and it would cut out at about 1.25. Thanks
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=329&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
you'd be better off
installing a two stage gas valve and a trigger device and once the pipes heat up, trigger low fire that fires just to the radiator load without the piping pickup factor..it is vapor after all..
http://www.maxitrol.com/Regulators/2stageregulators.html
Gerry:
Are you suggesting that the regulator you mentioned can be used on a single stage burner to allow it to operate as a two-stage burner?Steve from Denver, CO0 -
yup,
we do it on almost every one.