Biasi B-10 Series Wiring

Rick W.
Rick W. Member Posts: 30
Was wondering if alternatives exist for locating the aquastat on a Biasi boiler(B-4)? The immersion well on this unit is quite close to the vent(in the rear). Is there an adapter kit with a long temp. probe pigtail and well clip that would allow for mounting the control up towards the front side? Thanks for any info!

Comments

  • tccoggs
    tccoggs Member Posts: 9


    I noticed the same on my B10. I plugged the stock well and came out the supply with a 3" nipple to a 90 EL to ran vertical with a 4" nipple and finally a 1.5 x 1.5 x .75 tee where I mounted an Electrowell and Hydrolevel 3150 combination aquastat/LWCO.

    Did your B10 ship with a L4006 or a 7248?? If you have the 4006 and would like the extra features of a 7248, I have mine for sale, brand new.
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,562
    The

    7248 that comes with the B10 can be remote mounted.I'd be very leery of removing the limit control from it's OEM position in the boiler.What happens when a circ goes bad with the limit 8" from the boiler?

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • tccoggs
    tccoggs Member Posts: 9


    Even with a bad circ, do you really think the temp diff between the boiler casting and a pipe 8 inches away from the boiler is going to be night and day???

    Sure, it might be slightly different, but I don't think we are talking enough to be an issue. Look at the Utica Trifire and an example, they mount the 7248 on the riser comming out of the boiler and I believe the Burnham MPO has the same configuration as well.