Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Number of 1/2 pex radiant loops can be run off 3/4 copper pipe
ed m
Member Posts: 65
need to run 1200 ft of 1/2 pex for radiant heat, a new extentsion. there was radiant in the floor,demoed it all now need to run 5- 250 ft loops do not know if the existing 3/4 manifold in crawl space can handle it. radiant is off a 30 gal indirect.
thanks eddie
thanks eddie
0
Comments
-
Heat loss
What's your heat loss for the area Eddie?0 -
You're ok
You could actually run up to six 1/2" pex loops off of that 3/4" copper if you needed to.0 -
It really depends on the GPM required for the area/loops and proper selection of circulator with all items considered.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 919 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements