Number of 1/2 pex radiant loops can be run off 3/4 copper pipe
ed m
Member Posts: 65
need to run 1200 ft of 1/2 pex for radiant heat, a new extentsion. there was radiant in the floor,demoed it all now need to run 5- 250 ft loops do not know if the existing 3/4 manifold in crawl space can handle it. radiant is off a 30 gal indirect.
thanks eddie
thanks eddie
0
Comments
-
Heat loss
What's your heat loss for the area Eddie?0 -
You're ok
You could actually run up to six 1/2" pex loops off of that 3/4" copper if you needed to.0 -
It really depends on the GPM required for the area/loops and proper selection of circulator with all items considered.0