L8148E
EJ hoffman
Member Posts: 126
what was wrong the knuckle head who replaced the leaking pressure relief valve dripped solder on it,copper releif line, and a smidgen of it got into the unit through the low voltage knockout and shorted out the transformer. The cost of not knowing customer pays for parts and service charge, the cost of knowing customer gets free service call, new part, plumber gets lecture on dripping/wasting solder. I sleep better and customer thinks I am too honest
0
Comments
-
L8148E transformer
I installed a new boiler earlier in the summer for a customer. They went to turn the heat on today but it didnt fire. Went to customers house and found no power on the 24v side. Appears the transformer burnt out. Can I replace just the transformer on the control? Do I need a transformer just for the L8148 or is it the same as the 24v transformer I have on the truck already? Thanks in advance. Mickey0 -
Save yourself time, change the unit.0 -
Yes.....but
Is it a "special" 24v transformer or a standard one? If its a standard transformer why spend $200 for the control when the transformer costs $12?0 -
Why
Why did it fail? Installer error too bad, lightning insuarnce may cover it. If it just died and you put it in last summer it should be warranted.
Leo0 -
Mickey, be careful
as you could have something out of phase and burn out another transformer. Are you familar with phasing of transformer?0 -
Riight idea
Leo has the right idea. Before you spend any more money, understand what might have gone wrong. This way your not going to throw good money away.
My$.02
Glenn0 -
I don't think
It is field replaceable0 -
The transformer in the
L8148E is not field replaceable. You will need a new relay, however before I stuck a new relay in there I would determine what the problem is or you may just do in a nother transformer. In those transformers in the relay "Z" is hot and "TV" is common.0 -
I had the same problem with a transformer cooking on a control and it was a zone valve causing the short.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements