NEW T87 HONEYWELL T STAT? PROBLEM WITH SHORT CYCLING GAS STEAM
Isn't it adjustable? If it was a regular merc one I'd be looking at the anticipator setting.
NEW T87 T STAT SHORT CYCLING GAS STEAM BOILERS
I have had several customers that have installed the new
merc free t87 Honeywell on Gas steam systems and the boilers short cycle like crazy...used on Utica Burnham and Peerless..anyone else have this prob?0 -
NO IT HAS DIP SWITCHES IN THE BACK...NOT LIKE THE T87F
THAT HAD HEAT ANTICIPATOR0 -
dip switches
The dip switches on the back should be set to your type of heating equipment. Steam should be 1 cph, It's listed right on the back of the thermostat. I believe that they both should be set to "On" or both up, if I remember right.
Good Luck!
Ross0 -
Ross the switches are set the right way for steam...
Its still a mystery0 -
Ok, Thanks for checking, EG. Maybe the control on your boiler can't handle a power robbing thermostat, so either a isolation relay needs to be installed or trya battery powered thermostat, with a dry set of contacts.
Ross0 -
Power robbing stat
can be a problem. I read that somewhere else this week. It can drive you crazy. Just get a Focus Pro TH5110. The cost is almost identical and the cycle rate is adjustable. I think you want maybe 2 cycles per hour.
Ken F
- 86.7K THE MAIN WALL
- 55 Biomass
- 102 Chimneys & Flues
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.3K Strictly Steam
- 43 Industry Classes