"Q: Could I turn the diverter tee around so the cone points toward the flow and use it as the first tee instead of the second?

A: You could, and it will work because the same principle applies: the diverter tee increases the pressure drop along the main and creates flow in the branch.

However, with the cone facing into the flow, the water will be a bit more turbulent and, if you're using enough tees, you might have to use a larger circulator to overcome the additional pressure drop caused by the turbulence. That's why most old-timers put the diverter tee on the return side with the wide end of the cone facing the flow."

Comments

  • Just wondering,

    I have a 2 zone M/F system w/CIBB. I use H/B V110 ZVs and each main is 1" steel pipe.
    The system was originally installed w/supply side(cone facing flow) single M/F tees.
    I`m installing(finally) my own Prestige boiler and was wondering if anything (other than reducing any velocity noise) would be gained if I reversed the flow along the mains?
    It should still work, but if nothing be had I`ll leave it that way.
    Thoughts?

    Dave
  • Big Ed_4
    Big Ed_4 Member Posts: 3,017
    Monoflow

    I always put the tees on the return because I was taught it works better. Never knew the reason ( noise you say). But seen them installed on the supply with no problem.

    What I would do if there was no problem before ,is keep it flowing in original direction. Just to play it safe.

    I would also change it to two circulators and ditch the zone valves at this point.

    There was an error rendering this rich post.

  • Bruce_26
    Bruce_26 Member Posts: 27
    Return Side

    As I recall, return side installation of the Monoflo or Taco venturi was the recommended location in the 50's. The location on the return should give you a higher BTU output. There are tables to compute the BTU output based upon the circuit and branch diameters and other variables. I always thought that they were an elegant system that required some thought and preparation prior to installation.
  • Thanks guys,

    ya I know monoflo`s are better on the return side, but was just curious if anything would be gained otherwise.
    Was just wondering.

    Dave
  • Ken Field
    Ken Field Member Posts: 123
    Might be my imagination

    but I seem to have less air problems in baseboard and convectors when the tees are on the return side of the radiation. I think it could be because the first tee looks like an an air scoop.

    Ken F.