Another thought is, could the returns be clogged? Trying to suck the proverbial golf ball through a garden hose and all that.
:)
Another thought is, could the returns be clogged? Trying to suck the proverbial golf ball through a garden hose and all that.
:)
0
Comments
-
I have cleaned and skimmmed
my boiler several times and used boiler cleaner but the water line still bounces 1"-2". Any suggestions? I followed instructions to the T and was very patient. What else could cause this
0 -
If the near boiler piping is not correct or the piping is under sized it could cause water line problems.0 -
Its done to manufacture specs
and there is a dropped header. I also just noticed that water is trickling down from the top of the sight glass. How can I check my flame pattern. I use a A 75 80 degree in a Beckett AFG0 -
Clog retures
How Do I check for clog returns0 -
At the end
of the return, one hopes, there is a plug or a valve. (When I design a system, I specify a full port ball valve at each end which allows a hose connection for a power-flush.)
It occurred to me that you may have dry returns (returns above the waterline) which are less likely to fill with rust. They may be, but less likely by far.0 -
My returns go into my hartford loop
0 -
See if
that is flowing too. Is there a drain? You have a plug above it at least.0 -
there is a ball valve
at the bottom of the hartford loop0 -
Then Grasshoppa
you must use it
Seriously though, if there is a way to get a valve in the other end of the line (where it begins), you can attempt a hose flush. Not too much pressure as that will back up into your radiators potentially. Just enough to say that a gallon in at a certain rate, comes out at a certain rate.
Prove that and you have no clog.0 -
foaming/priming
If water is clean,then it could be priming.Is this a new replacement boiler?Are the pipe sizes leaving the boiler the proper size?Try this.allow boiler to cool,close outlet valve at boiler,start boiler,watch water line,see how long it takes to come up to operating temp/pressure.slowly open outlet valve,turn boiler on,what happens?you could also try shutting off the rad valves on a whole floor,start boiler,and see what happens.if boiler is ok with just heating 1 floor,then crack open 1 radiator valve at a time,see what happens.It could be that you are pulling too much load,causing the priming problems.need nore info on system size,operating pressures,etc....0 -
Im fairly certain its not to much load
there is only 6 rads for a boiler rated a 340EDR0 -
Clean out pig tail, clean out gauge glass valve tappings.0 -
Pigtail and sight glass clean as can be
0 -
steamer
if this is a new steamer,the newer steamers might not have a enough 'steam space',above the waterline,thus causing problems.What about the firing rate of the boiler?is this gas or oil. if burner has been downfired,or slightly undersized,along with undersized piping at outlet of boiler,it can be problems.if the water is clean,then it known as priming.if the water is dirty,it is foaming.it has to be one,or the other...I tried giving you troubleshooting tips by reducing the load,and watching the waterline.did you try reducing the load?without being there,my tips are easy to try....0 -
edr
you have to be sure...start from scratch....what is the edr ratings of the radiators? all rads totaled must not be more than the boiler......how about a heat loss on the building?...lots to consider....I have over 3o years with steam boilers....not trying to sound like an expert,but you expect a simple answer to your problem...why not hire someone to come and look at the system?0 -
Stewy is getting
a great workout, running up and down the stairs between e-mails.
We can call this "Holohan's 'Buns of Cast Iron' Workout"
Infomercial on HVAC-TV, 11:00 PM....
0 -
Very good workout indeed
I was trying to figure this steam system out thats why I haven't called on a pro yet but I'm getting there. Its very hard for me to admit defeat. My EDR for the total radiator load is 253 (not count the piping) and the boiler is rated at 340. After the boiler warms up the water to the aquastats 180 it takes 7mins to travel 8 feet in cold but insulated main w/2 Gorton #1 vents. All along the waterline bounces in the sight glass. I've skimmed and skimmed, used TSP and Pure Pro Boiler Cleaner that claims to stop priming and surging. No luck!! I'd like to do this myself (with of course all the help I can get from here) but, winter is coming so as a final resort, who knows a good steamer in N.H.0 -
I am having the same problem with a couple of Weil Mclain 1088s we just had installed.
I skimmed and skimmed but still had problems with the water line.
Just yesterday I steamed up one, shut it down and isolated it and then let the pressure drop down to zero.
I manually turned on the condensate feed pump and filled the boiler up to the top.
I opened the skim port and let it drain till it stopped. Then I cracked the manual feed just enough to let the water flow out of the boiler slowly. Then I left it running all night in our sump pit.
This did wonders for the water line. It is not perfectly stable but only bounces about 3/4" compared to 4' - 6'" before.0 -
skimming methods
why is it that no one has developed some sort of automatic skimming device?
every new boiler installation ,or major repiping consumes at least 3 hours of skimming with wasted hot water and someone needed to watch over the process.
isn't there a better way?--some thing automatic maybe separating the oil into a spin-on filter while we sleep!--nbc0 -
I'm in NH
Where in NH is the boiler?
Noel0 -
Dover, NH
0 -
Oooh
This sounds promising... If Noel is involved, I would sleep better at night.0 -
Yes
Noel is one of the best steam men out there. I think they still miss him at Colby-Sawyer.....
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
You already spotted the problem
You already spotted the problem, water trickling down from the top of the gauge glass. Skim it again and again.
Leo0 -
check this
flame impingement and overfire will cause surging also0 -
Thanks, gents
I'm 2 towns north of there. Contact me here, if you like.
http://steamheating.googlepages.com/home
Noel0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements