T-Stat with 2 relays
work this out by looking at some diagrams and get back to you.
0
Comments
-
T-Stat with 2 relays
I recently installed a New Yorker CG60 Gas / Hot Water Boiler. I have two zones, and am using 1 Honeywell R832A Relay , and 1 Taco (1 zone)relay to zone system. After wiring the relays from T-stats, I have a problem figuring how to wire T-stat to ignite boiler on temp. rise. Initially, I sent both T-Stat ( R&W wires for each T-Stat) wires to the R & G contacts on transformer. Problem is when I turn up one T-Stat, both Circulators turn on. Can you help? Thanks. Mike0 -
Mike the diagram
is being sent by e-mail.
The wiring should be to R and Y not R and G.0