Brad White_198
Member Posts: 72
The Hartford Loop may or may not be part of the issues. Think of the Hartford Loop firstly as a "safety seal" to keep water in the boiler should the return line leak.
A Hartford Loop should be installed on all such steam systems with few exceptions. If the boiler manufacturer recommends it, it becomes a code requirement in most jurisdictions. It is good practice regardless.
Secondly, the Hartford Loop can act, in concert with the wet return, as a seal to keep steam out of the return line. (Too often I have seen returns dropping down and connecting to the equalizer in a location that may occasionally be above the waterline, thus allowing steam to hold back any return condensate. A drop and rise would solve this.)
The make-up water usually goes into a wet return, yes.
A counter-flow system would normally have a drop to the return shortly after the main leaves the boiler, to drop off the returning backflowing condensate of course. You probably have this; if not, I cannot imagine how it works without a secondary means of return. Let's assume you have that.
The main vent should indeed go towards the end. Getting air out of the boiler is great, I would leave that as it does no harm, but it does nothing toward getting your main vented. Hold it back at least 15 inches from the end elbow though.
A Hartford Loop should be installed on all such steam systems with few exceptions. If the boiler manufacturer recommends it, it becomes a code requirement in most jurisdictions. It is good practice regardless.
Secondly, the Hartford Loop can act, in concert with the wet return, as a seal to keep steam out of the return line. (Too often I have seen returns dropping down and connecting to the equalizer in a location that may occasionally be above the waterline, thus allowing steam to hold back any return condensate. A drop and rise would solve this.)
The make-up water usually goes into a wet return, yes.
A counter-flow system would normally have a drop to the return shortly after the main leaves the boiler, to drop off the returning backflowing condensate of course. You probably have this; if not, I cannot imagine how it works without a secondary means of return. Let's assume you have that.
The main vent should indeed go towards the end. Getting air out of the boiler is great, I would leave that as it does no harm, but it does nothing toward getting your main vented. Hold it back at least 15 inches from the end elbow though.
0
Comments
-
Hartford Loop In a Single Pipe Counter Flow Steam System
I have a customer that has a Single pipe counter flow (reverse flow) steam system, and he has been having some problems. Most of it is air problems, but when I was looking at the piping there was no Hartford loop piped in. But do you need a Hartford loop in this particular system? Also, the water supply should best be installed on the return of the boiler? He also has his main steam vent about 3 linear feet off of the supply main, should I move this to the end of the run? ( about 25' )0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements