3 way 24v zone valve?
Rollie Peck_3
Member Posts: 24
If your system uses more than one pump, you could use one
120 volt relay wired in parallel with each pump and then
wire the contacts of the relays in parallel so that any one
of them connects the 3-way valve to a 24 volt transformer.
Rollie Peck
Homeowner
120 volt relay wired in parallel with each pump and then
wire the contacts of the relays in parallel so that any one
of them connects the 3-way valve to a 24 volt transformer.
Rollie Peck
Homeowner
0
Comments
-
3 way zone valve????
I have a Taco SR504 switching relay which is hooked up and running correctly with 4 zones. My problem is I have a 3 way 24volt valve that I need to wire somehow so that when one of the 4 zones, thermostats call for heat and turn on pumps, then opens the 3 way zone valve? Any help would be great.
Thanks
James0 -
3-way valve
One easy and inexpensive way to do it is to connect the primary of a 120V to 24V transformer in parallel with the pump and the secondary to the 3-way valve.
Rollie Peck
Homeowner0 -
Yes I have 4 pumps, 4 zones and 4 thermostats wired to my SR504. I just need something to send a signal or figure how to wire the 3 way valve so I believe the b port opens when one of the 4 zones call for heat.
Thanks0 -
3-way valve
Hi James:
The Taco controller will connect the two "X" terminals
anytime one of the pumps is energized, enabling the boiler burner to come on.
You could wire the 3-way valve across the gas valve if it is a gas boiler or the burner run relay if it is an oil burning boiler. However, the transformer in the boiler may not be able to handle the additional load. It could handle the additional load of a small relay with a 24 volt
AC coil, however. You could wire the contacts of the relay to connect the 3-way valve to an external 120v to 24v step down transformer.
I'd like to send you a drawing, but don't know how to do that on this website. Send me an Email at rol72@earthlink.net if you would like a drawing.
Rollie Peck
Homeowner0 -
I wonder if
maybe the normally open side of three way valve supplied the heating zones and the normally closed port would supply the priority zone DHW thats easy to get wired, one zone calls for heat valve opens, think about it?0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements