full bore zone valve
Brad White_198
Member Posts: 72
is comedy! :D
As for the valves, for low pressure-drop 2-position operation, we normally specify full-port ball valves with a motor actuator. Belimo offers these (also the have neat characterized ball valves for more proportional control).
Many ball valve manufacturers (Conbraco/Apollo, Watts, Neles-Jamesbury) offer models or adapter kits which can be fitted with an actuator.
Still, if you have a one-source supply for the entire assembly, that is where I would go. But in a pinch, if you have a ball valve already installed or on the shelf, you can usually get something working well for maybe less cost and hassle.
As for the valves, for low pressure-drop 2-position operation, we normally specify full-port ball valves with a motor actuator. Belimo offers these (also the have neat characterized ball valves for more proportional control).
Many ball valve manufacturers (Conbraco/Apollo, Watts, Neles-Jamesbury) offer models or adapter kits which can be fitted with an actuator.
Still, if you have a one-source supply for the entire assembly, that is where I would go. But in a pinch, if you have a ball valve already installed or on the shelf, you can usually get something working well for maybe less cost and hassle.
0
Comments
-
full bore zone valve
I'd like to get a full bore 1 1/4" zone valve. Anyone know of any?0 -
I've seen 1.25 White-Rogers
The 1300 series with the rotating stem will open about as wide as anything out there.0 -
Just what I was going to Say
The friction loss on the 1 1/4 inch valve is equal to 7 feet of 1 1/4 inch tubing. Just about nothing.
Boilerpro
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"There was an error rendering this rich post.
0 -
So does that mean I shouldn't be too concerned about the bore opening being too restrictive?0 -
Caleffi
Caleffi makes motorized ball zone valves in 1" with a Cv of 13. You can't beat Caleffi quality either.0 -
Thanks, I hadn't heard about these....NM
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"There was an error rendering this rich post.
0 -
WHITE RODGERS 1361-104
Would the 1-1/4" WHITE RODGERS 1361-104 with a cv rating of
42.2 be considered to have low restriction flow?0 -
Cv
Your head loss in feet with a given Cv rating can be calculated with this formula.
Head Loss (feet) = (1.52 * gpm / Cv)^2
So at 20gpm, the head loss through a valve with a Cv of 42.2 would be 0.51 feet. At Cv=13, the head loss would be 5.5 feet. Which valve you choose depends on the flow rate and what you are controlling.0 -
yes, very low
We used them at Sea World until the baby Harbor Seals escaped out thru the zone valves!0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements