boiler w/ b/u geo

mikea23
mikea23 Member Posts: 224
2 stage aquastat on buffer tank and inject in from boiler is the simple way. Pipe boiler with primary loop and pump from that into buffer tank. set aquastat 20 deg apart. I have done this 4 or 5 times it works great.

Mike

Comments



  • Geo w/ b/u oil boiler, we are currently bidding this project and trying to determin the best way to pipe and control any sugestions would be helpful.