combustion analysis guidelines for boilers
Jim_61
Member Posts: 3
I think these figures are a little off. In round figures, a 7.5% CO2 reading will give a corresponding O2 reading of 11% and excess air at 103% ... if you're talking # 2 oil.
Jim ...
Jim ...
0
Comments
-
When checking a boiler
That you have no manufacturer spec. sheet for. What parameters do you look for. I am doing a safety check on a couple of commercial boilers that I have not seen before this morning.0 -
Regarding generic readings
On gas I am usually looking for a minimum of 7-7.5 CO2 and less than 50ppm CO.0 -
Thats the kind of thing I need.
Kinda on my own here. I had never even heard of a combustion analyzer until I started reading Dan's books about four years ago. I even worked at a union shop for some time and no one used it. Just the fact that it shows the efficiency of any gas burning anything is a great sales tool.0 -
Testo
has an on-line PDF guide available which has good background and theory. I think I attached the correct one, they have two similar documents, I think.
This is all general/generic and the boiler you are testing may have specific parameters of course.0 -
That apropreate
My analizer is a Testo. Thanks0 -
You want
net stack temperature between 350 to 550 degrees F, O2 above 4% typically between 5 to 7%, CO2 at 7.5 to 9.5%, excess air 25 to 50%, draft -.01 to -.03. Now with some commercial boilers things may be a little different depending on the boiers. Most of those companies if you call and speak to engineering will give you the requirements for their equipment.
I would suggest you also get some training to help you out. Give me a call at 401-437-0557 or e-mail me and I can direct you to some literature and/or training0 -
I am talking gas
not oil.0 -
I can't
get the link to open... it says .pdf but it's some .cfm file which won't open. How did you open it?
Edited: in case someone else is having problems opening it, save the file and then change the extension from cfm to pdf and it will open in acrobat reader.... thanks Dave's plumbing and heating.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements