Oil Boiler sizing---specifially EK
narcaparbebra
Member Posts: 32
Thanks so much...just to make sure...your last sentence refers to issues of using oversized non-EK boilers, right?
0
Comments
-
Oil Boiler sizing---specifially EK
I've learned on this board that's important to get a heat loss calc and to match the load to the bolier size. According to EK specs, the smallest oil boiler they make is 104k. Does that mean if my house has a 60, 70 or even 80k btu loss that I shouldn't consider an EK? I noticed the gas/lp units get into the 70k range but gat/lp is not an option for us. Thanks!0 -
The EK
system manager control negates to a large extent the drawbacks of oversizing.An over sized boiler will have increased idle losses and short cycling.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"To learn more about this professional, click here to visit their ad in Find A Contractor.0 -
Yes
the manager gives the EK the least idle loss of any oil boiler and reduces short cycling.A house with multiple small zones will still cycle quite a bit however.The savings with these seem to be on par with any other though
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"To learn more about this professional, click here to visit their ad in Find A Contractor.0 -
3 firing rates
make the EK-1 able to go below the 102,000 and more toward 80k. It could impact domestic hot water production at that rate but it is approved by EK.
Ken
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Just to clarify Ken's statement re lower firing rates - these are specified for power venting only due to a lower stack temperature that would probably lead to condensation in a chimney.
In my own home I've had an EK-1 for about 11 1/2 years. Heat loss is approx 65K, 3 heating zones. I haven't really seen any issues with short cycling.0 -
Four Firing Rates
SPECIFICATIONS: EK-1 FRONTIER
Input Gross output AFUE Domestic Hot Water
.68 GPH 83,000 BTU/HR 87.9% 170 Gal /Hr.
.74 GPH 90,000 BTU/HR 87.7% 180 Gal /Hr.
.85 GPH 104,000 BTU/HR 87.5% 162 Gal /Hr.
1.00 GPH 121,000 BTU/HR 86.2% 228 Gal /Hr.
0 -
Chimney Venting
Just to clarify, the .68 and .74 GPH for the EK-1 are recommended for use in a power/sidewall vent only by Energy Kinetics according to their manual. The lowest input recommended for a chimney application is .85 GPH.0 -
What about
a stainless lined chimney. My take on that is that is that there is little or no condensation due to quick heating of the liner. If that is the case, the power vented firing rates may apply to a lined chimney. Maybe Hankinson will clear that up for us(me).
Ken F.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
I've
used the lower firing rate in lined chimneys as well as very short triple wall metal chimneys with no problem.Just watch your stack temps.The standard firing rate gives about 415 net
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"To learn more about this professional, click here to visit their ad in Find A Contractor.0 -
lower firing rates
Yes, the lower firing rates have been used with a chimney vent successfully, however not all of the attempts were successful. Therefore EK can't recommend them and won't stand behind the company that does so and has a condensation issue.
I also should point out that it's not just the firing rate that affects stack temp but also the CO2/02 setting. Higher CO2, lower stack. Lower CO2, higher stack.0 -
Lower firing rates
It's certainly not for every job and I wouldn't lower the CO2 just to increase stack temp.Depending on field conditions,it's another tool in the bag.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"To learn more about this professional, click here to visit their ad in Find A Contractor.0 -
I agree
It is hard on the combustion chamber when you increase the combustion temperatures that much, so there will eventually be collateral damage. I have several systems nearing 20 years with the original chamber. And others I see only a few years old have cracked refractory because they have not been adjusted correctly. I'm sure there is a happy medium but we usually stick to factory spec.
Ken F
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements