Heat source for small radiant job

Simply Red was on to something. Certainly you can use the X-pump block for the radiant loop, using the DHW heater as the primary heater, and the X-block as the interface secondary heater for the radiant loop. The X-pump block is equipped with an integral heat exchanger to prevent the DHW from interacting with the radiant medium. Providing you use an oxygen barrier pex tubing you can use ferrous components on the radiant side reducing initial setup cost. Incidentally, this is a great way to introduce a Hydronic system to a customer with forced hot air. For your reference I attached some literature on the X-pump block.
Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions

Comments

  • Jim P
    Jim P Member Posts: 29
    Heat source for a small raidnat job?

    I am doing a small radiant job with a btu loss of 13,000. What kind of heat source should I use? A previous contractor was going to use an instantanious hot water heater with 140,000 input( 10 times the btu power needed is a little overkill). I was thinking about an electric hot water heater. The customer does have gas in the house, and currnetly heats the house with forced hot air.

    Thanks,

    Jim
  • Mark_7
    Mark_7 Member Posts: 123
    small rad

    Lang make a combo electric heater unit with ciculator thAT might work just fine.
  • steveex
    steveex Member Posts: 95


    You have 3 options 1- solar 2- gas water heater 40 gal 3- very small gas hot water boiler. Your cost vary on each application. water heater system the cheapest, small boiler next and then solar with small indirect tank. Choose your weapon wizely.
  • steveex
    steveex Member Posts: 95


    I almost forgot, warmly yours has electric mats that lay on floors, under carpet, tile mud job or wood flooring, check it out i think its 10 amps for every 100 sf.
  • Simply Rad_4
    Simply Rad_4 Member Posts: 4
    Taco X block

    If the job has a DHW heater use a taco X block and if you have to, use a flow switch for priority for DHW. It works great, relatively easy. The Xblock is an all in one componet, including outdoor reset.
    Good luck
    Jeffrey
  • Mike Dunn
    Mike Dunn Member Posts: 189
    small power plant

    Both Triangle tube and Lochinvar have boilers that will modulate down in that area. 10K for the Lochinvar and 16K for the Triangle Tube

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Jim P
    Jim P Member Posts: 29


    Anyone have any experience with using an electric hot water heater say 50 gallon as the heat source?


    Thanks,


    Jim
  • Chris S
    Chris S Member Posts: 177
    small job

    I did an install using a 40 gallon electric- worked just fine- 12,000 btu load. My choice was based on future renovations that will include a boiler install.
    Chris

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"