What is it?
karsthuntr
Member Posts: 3
No it is not a rolairtrol. I should have put that in my post. :)
0
Comments
-
What is it?
I have a church with a leaking Burnham V9111A, it is leaking at the push nipples. I had the Burnham rep. out to look at it the other day and he questioned what a component on the system. It is a 180 deg. constant circulation system with two circ pumps. The expansion tank is the old style with no bladder. What you see in the drawing is all there is on this "tank" (for lack of a better term), it is completely insulated so I have no numbers on the tank itself.
So what is it?
http://farm4.static.flickr.com/3079/2781807676_9765d06007.jpg0 -
Does it look like this?
http://www.bellgossett.com/productPages/Parts-Rolairtrol-Air-Separator-For-Hot-and-Chilled-Water.asp0 -
similair to rolairtrol
B&G used to have a non ASME separator "IAF" with 2" or 3" threaded connections, so I think that is what you have.
Not been manufactured for a long time now.0 -
Do you have a link or picture?0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements