Thanks for your help Steamhead, I was a little unsure of the rating I had come up with comparing this radiator to a Triton wall hung, just didn't seem to jive....
0
Comments
-
WALL HUNG RADIATOR EDR W/PICS
Hey guys, looking for a square feet EDR rating for a wall/ceiling hung radiator, need this rating to size a new steam boiler. The radiator is 46" long, 15"wide & has 22 sections, I am attatching pics of this radiator, notice on the plugs there is some stamping, looks like it says NR-B CO.Thanks again guys for your help0 -
That looks like
a single-column rad without the legs. The standard leg height to the center of the tapping for column rads was 4 to 4.5 inches. Subtracting this amount leaves us almost exactly at the height (width) you measured.
Each section of this pattern would have a rating of 1.5 square feet per section. So the rad in the pics would have a rating of 33 square feet EDR.
The "NR&B" on the plug stood for Niagara Radiator & Boiler Co, which later became a part of National Radiator Corp.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements