Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
WALL HUNG RADIATOR EDR
MikeyB
Member Posts: 696
Thanks for your help Steamhead, I was a little unsure of the rating I had come up with comparing this radiator to a Triton wall hung, just didn't seem to jive....
0
Comments
-
WALL HUNG RADIATOR EDR W/PICS
Hey guys, looking for a square feet EDR rating for a wall/ceiling hung radiator, need this rating to size a new steam boiler. The radiator is 46" long, 15"wide & has 22 sections, I am attatching pics of this radiator, notice on the plugs there is some stamping, looks like it says NR-B CO.Thanks again guys for your help0 -
That looks like
a single-column rad without the legs. The standard leg height to the center of the tapping for column rads was 4 to 4.5 inches. Subtracting this amount leaves us almost exactly at the height (width) you measured.
Each section of this pattern would have a rating of 1.5 square feet per section. So the rad in the pics would have a rating of 33 square feet EDR.
The "NR&B" on the plug stood for Niagara Radiator & Boiler Co, which later became a part of National Radiator Corp.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements