Taco mixing block

Big Will
Member Posts: 395
I can't find any table that will show how many BTU it can mix based on the delta-t form system to boiler. Or any other BTU rating. I have a 180Kbtu copper fin on about 150Kbtu of in slab. I would like to run the boiler at 150-170deg. I just am worried that it will not be able to mix fast enough for that load.
0
Comments
-
RMB not big enough
Will, I just check the literature and it states "can handle radiant loads up to 120000 Btu's. I would suggest that you double check your heatloss, or change your delta T. This may help you out. Hope that helps.0 -
Have you looked at
the HBX HydroBloc? You can use it as a mixing valve with a built in 3 speed pump or you can hook it up P/S and use it as an injection pump to handle larger loads.
Ted0 -
Glad it wasn't a snake.
I looked at that sheet didn't see it. Thanks. The HBX control looks good for the job. Not a west coast product though. nearest rep is what appears to be a injection moulding plastic company in Oregon. I will give them a call on Monday to find the nearest hydronic rep.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements