Steam Pipe Return Replacement
Grant
Member Posts: 8
Is it OK to replace about 100 ft of 1-1/4" iron pipe with 1" copper as a return on a steam system in the floor on a slab (no basement)?
0
Comments
-
Condensate return
No,I would not recommend it. I would replace with schedule 80 1-1/4" welded pipe.0 -
Are you planning
to run the new pipe in the slab?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
the better job
might as well go the extra mile & use stainless.0 -
If below the water line
Type L copper should be fine, with the appropriate flushing fittings as you would do anyway. I would stay away from Type M and if I could find Type K, that would be better.
No argument against stainless though! Heck, why not. It would be interesting to see what Fe deposition does to it at least. Orbital welding would be a plus, just for fun! OK, kidding...
But at my heart, I agree with Joe Bertoldi, Schedule 80 steel is a long-lasting traditional approach. I take it that you fully understand that copper above the waterline in a steam system is asking for trouble.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements