Hartford Loop and Main Vent piping in one pipe steam - uh oh...
J.C.A._3
Member Posts: 2,980
#2 COULD be a problem, if you don't have the recommended distance from the waterline to the first elbow on the header(s). I like to see 24" minimum, but the manufacturer has the final say.
Pictures would be good. Chris
Pictures would be good. Chris
0
Comments
-
Hartford Loop and Main Vent piping in one pipe steam - uh oh...
Hi, I have 1 a one pipe steam system and have read all of Dan's steam books cover to cover.
I noticed what could be a few issues with my piping and could use your opinions. Thanks so much for your help from a homeowner trying to fix issues before it gets cold.
1) Main vent is 9" not the recomended 15" from the end of the condensate return where is drops to the boiler. It is a new vent and up on a tee 10" from the return pipe. The end of the return is right near my boiler so unless I redo the entire return pipe system this is as good as I can get it.
- Is this a big issue to not have it the 15" away?
2) Hartford loop. From what I understand the top of the loop is supposed to be a minimum of 2" below the waterline. In my case it is 1.5" from the top of the waterline. My Wiel McLain manual shows a waterline of 23 13/16th's.
- Should this be changed so that there is 2" or more from the top of the loop to the waterline...if so why (safety/efficiency etc.)?0 -
rest easy
#1- don't sweat it...#2- leave it alone its fine.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
Loop to waterline issue?
Hi and thanks for the replies guys. I have definately met the 24" min from waterline to the bottom of the header....it's more like 32"....it's the top of the hartford loop (Top of the "h"), that is 1.5" to the waterline instead of 2". What negative or drawbacks might happen when I fire up the boiler? Thanks0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements