circulator location
Glenn Sossin_2
Member Posts: 592
In my mind, the technical reason would be - as the mixing valve approaches the set temperature, the hot inlet side of the valve would start to close down. When it does - you have no circulation in your radiant loops.
Easy way to think of it always have the pump inside the radiant loop you'll never go wrong that way.
My $.02
Glenn
Easy way to think of it always have the pump inside the radiant loop you'll never go wrong that way.
My $.02
Glenn
0
Comments
-
circulator location
im doing a zone of radiant heat. the radiant manifolds and mixing valve are going to be approx. 30ft away from the boiler.so high temp feed and return going approx. 30ft.... in the diagram that i made for the job i put the circulator on the mix side of the mixing valve(about 30ft away from the boiler). a fellow i was talking to asked why i didnt leave the circulator at the boiler circulating towards the mixing valve (towards the hot side of mixing valve) and he claims that it would work the same.i have always put the circ. on the mix side of the mixing valve pumping away, and all diagrams i can find always show it this way. i got frustarated cause i didnt know the reason why. so heres the questions. 1.will it work both ways? 2. why is it better to put the circ on the mix side of the mixing valve (like i always have done)?0 -
Circ Location
When using a mixing valve you need to put the pump on the mixed side to create a positive pressure differential to "pull" the mixed water through the valve. You have the placement correct!0 -
ya i new i was doing it the right way but would the other way work? im looking for a technical reason as to why this way is better0 -
According to Brad White,
and I agree with his reasoning, "pushing towards" it simply becomes a diverting valve. "Pulling away" it is a true mix.
Dave0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements