Secondary pressure limit?
Home Depot Employee
Member Posts: 329
You would use the H/W L4079B1033 (2-15 PSI) which has a manual reset.
I would set at about 7-8 PSI, which is under relief valve setting to prevent nuisance tripping if boiler surges or partially floods.
I would set at about 7-8 PSI, which is under relief valve setting to prevent nuisance tripping if boiler surges or partially floods.
0
Comments
-
My steam boiler at home cycles between 1/2 and 2 PSI, which is at the bottom end of the Pressuretrol installed on it. It also has a 10 PSI relief valve . . . but no secondary overpressure switch to shut it down if the Pressuretrol fails. In an industrial setting, I don't think this would be allowed . . . or at least I wouldn't want it that way.
Should I install a secondary, manual-reset limit switch, maybe set at 3 or 4 PSI? If so, could somebody recommend a part number. I'm finding the on-line Honeywell catalog information to be a bit vague.
Thanks again!0 -
Perfect! Thanks!0 -
OK, now I have one - sort of.
Money is a little tight after all the major repairs I've done on my antique home this year, so I'm leaning toward saving myself a couple hundred bucks.
I got a couple of working Honewell PA404A Pressuretrols for $5 on eBay. They aren't manual reset, but they do operate in the 0-10 PSI range. I'm thinking I'll install one in conjunction with what I have, and just set it a little higher. Since it's not manual reset, I'll need to check it once in a while to make sure everything is working right, but it should give me that little extra measure of safety.
Am I nuts? Comments?0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements