Proper flue pipe size 3.5gph oil?
don_200
Member Posts: 4
Being I'm a hvac guy I would have to side with the boiler guy after all he the one that checked draft on a hot and cold chimney I would assume.
Maybe you need to check the size of the liner and see if it can handle the extra load.
Our oil company just cleaned our Smith Model 19 Series 6 boiler. I asked them to increase the nozzle size from 2.5gph to 3.5gph since it was steaming too slowly.
The tech told us the draft was inadequate and told us to get a chimney liner. Yesterday the chimney pro came and found that the chinmey has a 1-inch liner already. But the liner Tee goes to an 8-inch pipe to the boiler, at which point it goes to a 10-inch opening.
My boiler guy sayes the 8-inch pipe is fine. The chimney guy says we need a 10-inch pipe to the boiler. I don't know who to believe, but every joint of the 8-inch pipe shows black where the sheet metal was crimped, to I tend to believe the chimney guy more.
Should this boiler have a 1-inch pipe to the chimney? The boiler tech has been servicing this building for 20 years.Steve from Denver, CO0 -
two things that you need to know first
1-max. fireing rate for this boiler-can not over fire
2-what size is the breach at the boiler. if 10in. you have to stay 10 in.
one more, 20 year old or more i would thick about a new boiler0 -
Rick:
The boiler is designed for 6GPH. It was being simmered at 2.5GPH.
The breech has a 10" to 8 inch reducer, which makes me wonder.
So the pipe from the boiler to the chimney (10-feet long) is 8-inch. The oil company tells me that the boiler was shipped years back with the wrong size breech.
The chimney liner is 10-inch, shared with a gas water heater.
The boiler is nine years old.Steve from Denver, CO0 -
Smith Install Instructions
Smith Install Instructions for that boiler state the connector from the smoke hood to the chimney be the same size as the opening on the smoke hood. It does list different size smoke hoods but doesn't say which size to use with which number of sections. Looks like a call to Smith is in order. I would assume they sent the right size with a six section boiler but that is just an assumption.
Leo0 -
The Smith
19-6 (not 19A) should have come w/ an 8" diameter flue collar.
The 3, 4, & 5 were 7". The 19-7 was 9".0 -
Draft
If you do not have enough draft it is most likly because you do not have enough combustion air coming into the boiler room0 -
> flue collar.
> was 9".
Ron:
That's good to know, since it means the present 8-inch pipe is OK.
Thanks,
SteveSteve from Denver, CO0 -
Ron:
I guess that means the 8-inch pipe is OK.
Thanks,
- 85.7K THE MAIN WALL
- 49 Biomass
- 72 Chimneys & Flues
- 92 Geothermal
- 150 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 850 Plumbing
- 5.8K Radiant Heating
- 372 Solar
- 14.5K Strictly Steam
- 58 Water Quality
- 39 Industry Classes
- 15 Recall Announcements
