furnace room air intake

Techman
Techman Member Posts: 2,144
bill, is this oil or gas?It could be 3,000 btu's per sq. in of "free air opening" NOT grill size or it could be as high as 6,000 btu's per sq in.Also a high and lo air opening might be required.Check w/ the furnace mfrg for their requirements.Primary air? Secondary air?Atmospheric burner?Fan assist?Tight furnace room?Ect,ect!Being a semi-pro(fishing doesn't count) you want to get this right!

Comments

  • bill_67
    bill_67 Member Posts: 29


    i am rehabing a furnace room, the hole in door for air looks like a drunken beaver put it in,would like a flush mount grill or vent cover,zero options shopping locally,any
    web sites to recommend.
  • Rich Kontny_3
    Rich Kontny_3 Member Posts: 562
    Sizing

    Is more important than looks as an undersized make-up air source can have very negative effects on firing and even CO levels. Have a proffessional give you the proper size and then look for an attractive grille.
  • bill_67
    bill_67 Member Posts: 29


    while i am new to the biz and i commercial fish 6 months of the year (the summer) i guess i am considered a prof., the unit ran fine (#s checked) this is purely cosmetic,
    just looking for site with a selection of sizes so i can
    size to fit.
  • bill_67
    bill_67 Member Posts: 29


    i guess my point is not getting through,i am a licensed oil heat service tech, i have passed the silver test in massachusett's,i have a one horse company in rural alaska that i only run in winter when the demand is such that the year around
    guy's can't keep up,having said that back to the original request,i am looking for a grill or air inlet cover that looks better than the previously mentioned beaver chewed one that is in the door,i am well aware of the air implications,just do not have current access to a distributer for these and was asking for directions.for the record the unit is running fine this is purely a cosmetic thing