lochinvar venting question
Kevin O. Pulver_2
Member Posts: 87
but I don't think I've ever seen anything using a 6" in photos or anywhere. The biggest I've done is a KBN399 which used 4". If my cummins diesel can breath through four inch pipe, surely the lochinvar can?
Kevin
Kevin
0
Comments
-
lochinvar venting question
when installing the knight 500 using the concentric vent kit cvk3007,the "y "concentric fitting is 6inch .can a 6x4 bushing be used to reduce the combustion air side or should it remain full 6inch for a specific distance before reducing to 4inch which is at the boiler? i cant find the answer in the install manual...not sure why the "y" supplied wouldn't be a 6x4.thank you in advance for any responsesThere was an error rendering this rich post.
0 -
IOM says:
Both combustion air and vent are run in 4", reduce at the concentric kit per the IOM page 18.
Found here: http://www.lochinvar.com/Resources.asp?res=IO&cat=B&prd=KBX0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements