lochinvar venting question

Kevin O. Pulver_2
Member Posts: 87
but I don't think I've ever seen anything using a 6" in photos or anywhere. The biggest I've done is a KBN399 which used 4". If my cummins diesel can breath through four inch pipe, surely the lochinvar can?
Kevin
Kevin
0
Comments
-
lochinvar venting question
when installing the knight 500 using the concentric vent kit cvk3007,the "y "concentric fitting is 6inch .can a 6x4 bushing be used to reduce the combustion air side or should it remain full 6inch for a specific distance before reducing to 4inch which is at the boiler? i cant find the answer in the install manual...not sure why the "y" supplied wouldn't be a 6x4.thank you in advance for any responsesPat0 -
IOM says:
Both combustion air and vent are run in 4", reduce at the concentric kit per the IOM page 18.
Found here: http://www.lochinvar.com/Resources.asp?res=IO&cat=B&prd=KBX0