trane direct return trap
c rafferty
Member Posts: 3
replacing a boiler, two pipe wet return. the system is a trane steam system. installed and fired with coal originaly, gas fired boiler installed in the early 50's. my problem is the direct return trap was thrown out with demo. would like to get my hands on one or cuurent equivlent. any idea's on how to keep the system original.
0
Comments
-
You can get by without it
though I would certainly never use that demo crew again!
Instead of a Pressuretrol on the new boiler, use a Vaporstat that cannot be set higher than 1 pound. I think the Honeywell model# is L408J1009. Set it to 8 ounces or so, this will keep the pressure low enough that the Return Trap won't be needed.
"Steamhead"
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
I have one....
But Steamhead's right, you don't need it.
Noel0 -
trane direct return trap
thanks for the info. also spoke to richard levi and he confirmed what you told me. thank you again.
c rafferty0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements