Hydrocoil sizing
mtfallsmikey
Member Posts: 765
The truth Steve...It WAS more nerve-racking than my daughters being born...must be old age.
0
Comments
-
The correct EDB
For residential purposes,what would be the correct EDB temp. to base sizing of a hydrocoil on?0 -
I would say probably 68
If this is on condensing boiler size the coil as large as you can. I try and size around 130 to 140 entering to stay in condensing temps. Keep a high delta t also on water side to stay in condensing also as long as you can keep your air temp up. I usually end up with more like heat pump air temps w/ this kind of sizing to stay in condensing but works well.0 -
I agree
for heating, your room setpoint if we are talking heating and no entering ventilation air.
Get all of your variables, BTU load, airflow CFM, water temp. in, water temp out, flow, entering air and leaving air. Technically you can heat a room with 80 degree air if the distribution is nearly perfect and there is enough airflow, but I typically strive for about 110 degrees to avoid wind-chill effect if it is dry.
With low water temperatures you may see a 3-row or 4-row coil. Manage the flow well and watch condensing happen.0 -
What is
EDB?Retired and loving it.0 -
I think
i think he meant entering drybuld temps.Should be EDT.0 -
Thanks!
If I don't ask, I don't know.Retired and loving it.0 -
To clarify:
EDB / EDT, also LDB /LDT, are interchangeable, as well as wet bulb acronyms. Depends on how they are listed on a mfr's spec. sheet. The unfortunate thing that I have found out during this particular science project is the lack of good air static pressure drop data for these coils, especially if you want to mount one of these in an existing forced air system in conjunction with an A.C. or heat pump coil...another question is can hydrocoils be mated to high-velocity A.C, systems? (good question for Mr. White!). While at the 'ole wholesale house yesterday, I wanted to price a couple of Taco circs, counter man was puzzled by IFC...sez he never heard of them!!....Arrrgh!0 -
And..forgot to mention
This will be hooked up to a wood-fired boiler. Not thinking real clearly this morning; my youngest daughter will be entering the hospital later this morning to have her son, my first grandchild...I'm kinda nervous!0 -
Wow
Tim,
May I ask - when you size for 130-140 entering water temp, is that at outdoor design temp?
I have four row coils and have set my curve so that at average winter temp in my area (35 degrees) the return water temp is not higher than 128; roughly speaking where condensation starts/stops. That translates to a boiler setpoint in the low 140's.0 -
hydrocoils
Of course they can! Just use the coils Spacepak or Unico or any other HV system offers; they're designed for the SP & Velocity.0 -
Mikey
If it's any consolation, I was way more nervous about my babies having babies than when we had the babies in the first place. All has turned out well and Grandkid #10 is in the oven as we speak. There is truly nothing like 'em.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements