Flat plate heat exchanger

Tom Hopkins
Tom Hopkins Member Posts: 554
Thanks Hot Rod. This is what I thought.

Comments

  • Tom Hopkins
    Tom Hopkins Member Posts: 554


    Just want to know if there is a possibility of damaging a flat plate heat exchanger when only one pump is running. That is, the input pump circulates while the output is stopped.

    Thanks,
    Luc
  • hot_rod
    hot_rod Member Posts: 23,371
    fluid on both sides?

    what kind of operating temperatures?

    hr
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Tom Hopkins
    Tom Hopkins Member Posts: 554


    It is between 140F and 180F on the input side. There is a glycol solution on the output side.
    Luc
  • hot_rod
    hot_rod Member Posts: 23,371
    I don't

    see a problem, check with the manufacturer to be certain. If it is a brazed plate HX it is assembled under much higher temperatures.

    180F is not too high to stress the glycol, either.

    hr
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Tom Hopkins
    Tom Hopkins Member Posts: 554


    Thanks hot rod. I thought the same thing but I wanted to check out with someone on the Wall.

    Also, I just want to say that I appreciate your articles in Phc News. I am looking forward to your future webcast on solar radiant.

    Regards,
    Luc
  • hot_rod
    hot_rod Member Posts: 23,371
    It may thermo siphon

    also, on the "off" pump side. Unless you have good check valve or flow check protection.

    hr
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream