oil boiler w indirect HW: summer settings?
nick_7
Member Posts: 15
I have a large weil mcclain oil boiler to heat a big house in NE w. indirect HW? do I need to change any settings on the boiler for the summer when it only fires for the HW? thanks
0
Comments
-
Controls
The boiler should have a control that only fires the boiler when the indirect tank calls for recovery. We usually use a Tekmar 150 setpoint control. The boiler should be wired for a "cold start", and not maintain a constant temperature. Hpefully, you have an outdoor reset control on the boiler to manage the system temperatures. If you don't have one, you'll find that the OD reset control can save an additional 10-20% of the yearly fuel costs.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0