I am considering installing an Axeman-Anderson coal fired automatic stoker boiler to our existing oil fired boiler so either or may be used depending on fuel situation. Any words of wisdom on the tandem or duplex piping?
0
Comments
-
Make sure
the normal waterline of both boilers is the same. This way the "A" and "B" dimensions will not change.
Pipe each boiler with its own header and Hartford Loop, then run the steam lines from both headers to a common header, as illustrated on page 67 of "The Lost Art of Steam Heating".
Install a king valve on each boiler header output, and a valve on the line leading to each Hartford Loop. This will let you isolate either boiler from the system when it is not in use.
Wire the system so only one boiler can be operated at a time.
I'm sure there are more details to be added, but these are what came to mind quickly.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements