Noise from radiant emission plates,
hot_rod
Member Posts: 23,400
could be the tube expansion in the groove, or the plate to floor attachment method.
Loose or not enough fasteners will allow too much plate movement and noise. Determine which is the cause.
Limiting the temperature swing, especially wide and quick ones as Paul suggested should help either problem.
hr
Loose or not enough fasteners will allow too much plate movement and noise. Determine which is the cause.
Limiting the temperature swing, especially wide and quick ones as Paul suggested should help either problem.
hr
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream
trainer for Caleffi NA
Living the hydronic dream
0
Comments
-
emission plate noise
I have a client who is complaining about noise in radiant staple-up w/emission plates. Any suggestions. G C has removed sheetrock in room with the problem.0 -
Plates
Are these the sheet metal "Omega Plates" or extruded aluminum plates? Does the system have outdoor reset?0 -
extruded aluminum, w/outdoor reset0 -
Couple More Questions
What brand and type of pex? What brand of plates?0 -
infloor0 -
infloor plates and infloor b-pex0 -
Are they susing setback?
0 -
Radiant Side Track
One thing I know about pex and extruded plates is that the fit has to be just right. Too tight and it wont go in, and too loose and it makes noise. I think the Radiant Side Track probably falls into the latter category.
What to do now? I would run the system with constant circulation on the lowest heating curve possible. Other than that, there isn't much you can do other than to glue all the tube into the track, which is a horrible mess.0 -
OD reset + automixing
We've fixed many of these systems with plate noise. A 3 or 4 way mixing valve and motor needs to be installed. This prevents hot slugs of water hitting the tubing and plates on startup. A gentle flow of modulated water temps reduces the "ticking" sound with dramatic effect. OD reset on the boiler only usually doesn't work.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
I did a job
I did a job with concrete embedded tubings and stapled up with alum plates at differnrt temps. Customer said it made noise during the first year and thereafter its fine.. As I learned from others and here, usually the first year the tubings make expanioson noises and then stop0 -
emission plate noise
This job also has thin slab and staple-up w/plates. It also has od reset and modulating mixing valves, tekmar controls w/logic, Munchkin 199 LP0 -
Transfer plate noise
If you are using outdoor reset and constant circulation you should not be getting any noise. Sounds like you have a thermostat in the system and that will give you the noise. Radiant floor should be modulated and run at the lowest possible water temperature not turned on and off. Constant circulation will give your customer the best comfort and efficiency. We use Hydronic Alternatives perc pipe and radiant side trak plates. The pipe does not give any expansion noise but we also spray 2 inches of close cell foam over all plates, piping and floor.
This gives great, even heat transfer and will not let the heat drop down. It also drops the water supply temperatures down below 100 degree's f at 20 below. Also it won't let any pipe move whatsoever. You should ask your tubing tubing manufacture if foam can be sprayed on it. Most don't like it , they are afraid the chemicals in the foam won't react well with the pipe. Hydronic Alternatives will stand behind their product. I have read a few articals lately on the increasing failure rate of B pex so I probally would not foam it. Good luck0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements