Steam Velocity

are they? What make and model?

What header sizes are recommended for these individual boilers?

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • TK03
    TK03 Member Posts: 54
    Steam velocity

    What is the maximum velocity in headers and steam mains. I have heard both 50 and 60 fps in mains and 30fps in headers. I need to size a header for tying together two steam boilers. Thanks in advance
  • Boston_2
    Boston_2 Member Posts: 107
    half the story

    Consider the condensate also if there not both on line.
  • kamney
    kamney Member Posts: 15


    2 MST629 boilers with 3" headers.
  • Steamhead (in transit)
    Steamhead (in transit) Member Posts: 6,688
    I'd use

    a 4-inch main header and drop the 3-inch outputs from each boiler header into that. Drip the end of this header the same as you would a boiler header, but run your drip to the system side of the individual boilers' Hartford Loops.