P/S Max GPM?
Blackoakbob
Member Posts: 252
That's what I'm after, I will check out Taco, thanks. My plan is to tie three boilers to an existing system via the hydro separator. Your project sounds great. What did you use for boilers,if I may ask. Best regards, blackoakbob
0
Comments
-
P/S Max GPM?
Is there a maximum gpm limit on primary/secondary? I planning a job that may require 150 gpm total when all of the modcons are on. Also, would there be a significant PD across the IE. Caleffi unit? Thanks in advance. Best regards, blackoakbob0 -
No Limits
The principle of P/S piping is just that, a principle. It does not bow to size.
FWIW, I have recently completed a P/S system using two boilers handling 358 GPM each, feeding into a common HW system system with variable flow. Not a problem.
Oh, if you are looking for a larger flow rate low loss header, Taco has a line, 5900, which goes up to, well, name it pretty much, at least 12 inches, if memory serves.0 -
Hi Bob
The boilers were gas-fired Burnham V-1118's serving an elementary school formerly served by a 1956 Fitzgibbons fire-tube steam boiler.
I am now looking at retrofitting a series of five Aerco Benchmarks (2.0 MMBH input each, 90 GPM each) using a Taco hydronic separator. System was supposedly P/S but not really.... :P
The Taco unit in that size should be a neat fix, I think.0 -
12\" Taco Green Hydroseparator?
Sounds like a giant Hydronic sepository for proper flow.
Paul0 -
the caleffi hydro seperator is avail in 6\" and 8\"
it's almost always the better way to do this - the bell and gossett people took one look at the Caleffi and they are selling it under their label - (they paint the non insulated ones red i suspect many others will follow, it just makes sense and when you think about the air and dirt separation effect combined with this huge point of zero pressure change, it also makes dollars, not to mention the fact that to do close-Ts correctly, you need 6 primary pipe diameters on either side of the tees a bit long with 4 pipe0 -
Couldn't fird..
the Taco hydroseparator on the Taco website last night. I'll check again tonight. Are they calling it a "hydronic bridge"? I haven't been able to locate a local ( Minnesota) rep for Caleffi, most of the sales people say, "Who?"
Are they usually sized by the pipe size or gpm?
Best regards,
Happy Mother's Day!
blackoakbob0 -
Caleffi has
supplied 10 and 12". I believe we have a 16" in the works for a special order. Your local rep or dealer should be able to get a price for you.
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Taco 5900 Series
Hydrolic Seperator - here is the link:
http://www.taco-hvac.com/uploads/FileLibrary/400-2.8.pdf
0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements