OT--Plumbing ???

Ed Lentz_2
Ed Lentz_2 Member Posts: 158
Thanks Ron for the heads up. I knew having that so close was going to have a "Gotcha"

Comments

  • Ed Lentz_2
    Ed Lentz_2 Member Posts: 158


    I am piping a new tub faucet. it comes down within about 5 feet of my superstor. Would it be kosher to get my supply cold/hot from the input and the output of the superstor? Something in the back of my mind says maybe I shouldn't for some strange supply/demand issue. Any thoughts greatly appreciated!

    Thanks
  • bill_97
    bill_97 Member Posts: 172
    Just watch out

    for some backfeed of hot water through the cold pipe if it's teed close to the Superstor . That happens from time to time and we use a simple flap check on the cold pipe of the heater to fix that problem .
  • bob young
    bob young Member Posts: 2,177
    heat sink

    piping arrangement provide 27 " thermal loop heat sink in lieu of check valve. problem solved