Vitorond 100 recall
Options
JayMcMann
Member Posts: 1
Has anyone heard about a recall for the Beckett NX burner used on the Vitorond 100 boiler and the SS insert
Thanks Jay
Thanks Jay
0
Comments
-
There's
no recall.The early NX NLEA without the mica window would sometimes have cad cell ohm readings higher than normal. Without the stainless insert some boilers would be problematic. Installing the insert and new NLEA are quick and easy.
I never installed an early one without the insert but I have serviced them and not all exhibit any problem.If yours does, call Viessmann
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0