Largest Sunrad
Al Corelli_2
Member Posts: 395
Ran into one of those customers that just HAVE to have the radiators recessed into the wall. Spoke to them about blowing in insulation and doing the windows over, but all they want to know about is how much "space" they can glean from recessing the rads. The disclaimer on this proposal will be very humorous indeed.
What is the largest Sunrad that can be installed on a 1" riser on the second floor of a small house. 4 rads total. The boiler has plenty of capacity. Mains are adequate. I'm looking for experienced installs. I want to see if I am being too conservative with my sizing. And, no, we cannot "wreck the wallpaper" to get new, larger risers up to the second floor.
All assistance appreciated.
I am || this close to firing this customer.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=449&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
What is the largest Sunrad that can be installed on a 1" riser on the second floor of a small house. 4 rads total. The boiler has plenty of capacity. Mains are adequate. I'm looking for experienced installs. I want to see if I am being too conservative with my sizing. And, no, we cannot "wreck the wallpaper" to get new, larger risers up to the second floor.
All assistance appreciated.
I am || this close to firing this customer.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=449&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
There was an error rendering this rich post.
0
Comments
-
Steam heat?
Is this hot water or steam heat?0 -
Single pipe Steam
Sorry.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"There was an error rendering this rich post.
0 -
radiator tapping list --one pipe steam --
Rating from an old burnham chart----- 1 " up to 28 sq. ft. 1 1/4 " 29 to 62 sq. ft.0 -
I would keep it under
45 sq. ft. EDR.Retired and loving it.0 -
Dan , did I mis interpret or is burnham wrong ?0 -
Can't speak for Burnham, Bob.
My number is from "Lost Art."Retired and loving it.0 -
Thank You!
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"There was an error rendering this rich post.
0 -
one inch
valve should be 1 1/4 " or gate. i " valve bet. 20 & 28 sq. ft. max. pg. 91 "lost art"0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 914 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements