plugged guage?
BRIANJ
Member Posts: 118
I have the same issue with my Peerless installed last September. Hope someone responds.
0
Comments
-
plugged guage?
I have a residential Peerless steam boiler and after the unit has been off for an hour sometimes, the guage still reads anywhere from 1-5 pounds of pressure. It was a new install in October.
Could it be clogged? need a new guage?
It is a round guage that reads "internal syphon" and psi below that.thanks guys.0 -
Probably is
the trouble with "internal syphon" gauges is that once the syphon clogs, it's all over.
Get a standard brass pigtail syphon and a standard gauge. If the pigtail under the Pressuretrol is iron, change it to brass also.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0