Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
plugged guage?
BRIANJ
Member Posts: 118
I have the same issue with my Peerless installed last September. Hope someone responds.
0
Comments
-
plugged guage?
I have a residential Peerless steam boiler and after the unit has been off for an hour sometimes, the guage still reads anywhere from 1-5 pounds of pressure. It was a new install in October.
Could it be clogged? need a new guage?
It is a round guage that reads "internal syphon" and psi below that.thanks guys.0 -
Probably is
the trouble with "internal syphon" gauges is that once the syphon clogs, it's all over.
Get a standard brass pigtail syphon and a standard gauge. If the pigtail under the Pressuretrol is iron, change it to brass also.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements