Using a fairly accurate infrared thermometer, or equal, regularly check different points on the return piping (where you can get at uninsulated iron) for temperature, and chart them on paper. Note outdoor temp with your record keeping, as the returns temperature will go up and down with the weather. Bad traps cause the temperature to just go up and up. You'll notice right away, if you get to know what is normal running temperature. Returns can run surprisingly cool.
Noel
Noel
0
Comments
-
Difinitive Steam Trap Testing?
Hi Everyone,
We are located in Spokane, WA and I am researching for my department to find out if there is a DIFINITIVE method of testing steam traps. I have been into this for less than a day, and quite possibly dumber about it than I was when I started. I have discerned that there are three accepted methods (visual, temperature drop, and listening devices, oh and acually a fourth which would be real time monitoring) but have not found anything pointing me toward the best, most useful, or choicest method. I thought I'd very much like to hear what you gentlemen have to say on the matter.
Thanks
Don0 -
We used an "electronic sthescope" with good results once we got the hang of it.
ED0 -
A Difinitive Answer?
Thanks for the responses guys......but this did not help. I need to know how to walk up to a trap I've never seen before, and tell whether it is bad or not. How did you use the stethoscope? What told you that the trap was bad?
Thanks Again,
Don0 -
infared thermometer
just point at incoming and exit piping. Instant response. temperature difference will depend on several factors - but the underlying note is that you will have a measurable temp difference for a correctly functioning trap.0 -
we use this
http://uesystems.com/prod_up_100_kit.asp
specifically the UP100C
after using it you'll want to smack yourself in the head for attempting to use any other method.
with this stethoscope, a functioning trap makes a sound like gurgling water every couple seconds when it opens and a click when it closes. a bad trap sounds like 100 PSI of steam basting through a 1/4 inch hole (even if your only running 2 PSI.
Its expensive ($1000) but worth it if your gonna be testing traps.
If your in a building with many failed traps, steam can be backing up though the returns, equalizing the temperature on both sides of a good trap. an infared thermometer cannot distinguish this from a bad trap. the ultraporobe can
also i have used it to find failing wet rotor circulators before they lock up.
also it great0 -
Now That's Difinitive!!!!
Thank you for the posts guys. The $1,000.00 hurts but That Is Difinitive!!! Great Answer!! Thanks Again 8-)
Don Smet0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 100 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 101 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 934 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements