Using a 3-speed circ as an injection circ?

Options
Rocky_3
Rocky_3 Member Posts: 232
done it multiple times. By dialing in your injection rate with the appropriate speed, you can actaully improve the "rangeability" of your injections system.

Rocky

Comments

  • Mike Lampkin_2
    Mike Lampkin_2 Member Posts: 124
    Options
    Using a 3-speed circ as an injection circ?

    Is it possible to use a multi-speed circ such as a 3-speed Grundfos ups15-58 or a Taco 00R-IFC as an injection circ rather than using a standard single speed circ?
  • Home Depot Employee
    Home Depot Employee Member Posts: 329
    Options


    Absolutely,

    Poor mans injection pump (can only dial it in close, not adjust for system & demand changes and bangs on and off versus variable)
  • Terry Trommeshauser
    Terry Trommeshauser Member Posts: 34
    Options


    you can still hook up these pumps to a mix control to vary the speed accordingly on supply/demand temps
    such as tekmar T356, etc.
    we've done this with great results.

    the 3 speed selection as per above does narrow the "range" nicely.
  • Rocky_3
    Rocky_3 Member Posts: 232
    Options
    Yes, still hooked to VSI control

    Did not mean to imply above that you did not have it connected to a VSI control of some kind. Without the VSI control, well, lets just say there is absolutely NO rangeability.
    Rocky
  • Mike Lampkin_2
    Mike Lampkin_2 Member Posts: 124
    Options
    Thanks everyone..

    Yes I'll be hooking it up to a Tekmar control.Thanks for the info.If you are carrying a 3-speed in your truck,it could also get you out of a bind if a vsi circ goes down and you don't have a replacement.
  • JohnNY
    JohnNY Member Posts: 3,231
    Options
    Wait a second...

    The responses here suggest this is a good idea.

    Wouldn't the speed selection (other than "high") limit the high-speed range, thereby limiting the functions of the VSI controller?

    Why would you willingly do that?





    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
  • Mike Lampkin_2
    Mike Lampkin_2 Member Posts: 124
    Options
    Whose Circ?

    Hi Rocky,
    Do you remeber if it was a 3-speed Taco that you used? I got a call from Grundfos today and they told me not to use the UPS 15-58.Apparently you can't use it because of the way it is internally wired.