Zone valve or circulator for an indirect heater ?

Ron,
By the expandable board and put the indirect on zone 6 priority. We do it all the time with low mass oil fired boilers like the biasi. I think you will be very satisfied nice to see you trying zone valves. As a cheap upgrade you can sell a taco pc 700 outdoor reset control that plugs into the sr board.

Comments

  • bill_97
    bill_97 Member Posts: 172
    We'll be installing a 4 zone gas boiler soon

    3 zones are heat and 1 is for an indirect . We'll be using a Taco 6 zone panel relay made for zone valves .

    Is there any downside to using a zone valve for the indirect ? We'd use a 1 inch Honeywell sweat zone valve . If we use a separate circ for the indirect it will have a weighted 1 inch flow check on it . Which I'm thinking might restrict the flow as much as a zone valve would ?
  • kevin coppinger_16
    kevin coppinger_16 Member Posts: 6
    Ron...

    I have done this a number of times w/ a super stor contender 50...2 1/2 bath home...no complaints. I even did it once w/ a smallish utica gas boiler and a SSC 80...they never run out and that was w/ a 72" soaking tub.
    it depends on how many people are in the house....
  • Ross_7
    Ross_7 Member Posts: 577
    1\" Zone valve DHW

    Hello Ron,
    I've used 1" zone valves on DHW with priorty with no problems at all. I have the same set up at my house. I usually use Honeywell, Erie, or Caleffi. Mainly something that's a little quicker acting than the heat motor 571 Tacos, which are fine for the heating zones,but if there is a demand on the indirect, somtimes waiting for the 571 takes too long. Just a suggestion, and remember to play "Smokestack Lightning" by Soungarden in the background while installing this setup or you may anger the boiler install gods! :-) Good Luck!
    Ross
  • bill_97
    bill_97 Member Posts: 172
    The PC700

    is also being istalled on this system . Nice control and easy to set up .

    I'd love to use all zone valves for anything over 3 zones , as long as we use the multi relay with it . Thanks Mike .
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,562
    Ron

    The conventional wisdom is to use pumps but I have done this numerous times for various reasons and never a problem.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • bill_97
    bill_97 Member Posts: 172
    We're using the same indirect

    with a Burnham Series 2 ? I don't know the gas model numbers . That is good to know that they have plenty of hot water . I'm pretty sure this house has 2 or 3 baths . Thanks Kevin .
  • bill_97
    bill_97 Member Posts: 172
    Honeywell

    is the brand of zone valve we install . Very reliable , for the limited amount we pipe in . I'll remember to play that song in my head when I vent out the gas main . Funny you mention Soundgarden . I was listening to A-Sides today on my Ipod while I was at the sump , kicking a football for my Lab and his friends to chase down . He'd be great on special teams . Thanks Ross
  • bill_97
    bill_97 Member Posts: 172
    Robert

    Yeah , I'm thinking the same thing . If you look inside a 1 inch zone valve , the opening seems pretty small . But when you look at how much room there is for water to pass inside a flowcheck , I bet the resistence is around the same .
  • Andrew Hagen_2
    Andrew Hagen_2 Member Posts: 236
    Cv

    Just a note, many 1" zone valves have the same Cv as their 3/4" counterparts.
  • Rocky_3
    Rocky_3 Member Posts: 236
    Install tempering valve if using zone valve

    I have been to far too many jobs where the zone valve has failed open and the hot water tank is the same temperature as the boiler. There was actually 2 lawsuits due to scalding injuries because of this issue. thats why I only use pumps for indirects....if the pump fails, all you get is cold water, not 180 degree water. Just my two cents worth.
    Rocky
  • Bob Bona_4
    Bob Bona_4 Member Posts: 2,083
    depends

    on the indirect. I assume you are using the OEM 007 for all four zones? Some indirects need a pump w/ a different curve to get r done.

    I personally would use a dedicated pump.
  • I vote pump...

    mass flow equals overall efficiency. Maybe only 2 to 5 % in your case, but with a series 2 every little bit helps, no?

    Ron, I have to tell you. I don't miss wrestling with cast iron boilers. Not even taking them out. We hire that out.

    When moving in to the job, if the boiler goes to the basement, we duct tape the boiler to the back of the apprentice and send him packing...:-)

    When he gets to the basement, he sees the square on the wall where the boiler is supposed to be, and there is velcro on the wall AND the boiler. He takes a run and leap, doing a 180 degree twist, and sticks the boiler RIGHT on the money.... Lets see you do THAT with a cast iron boiler ;-)

    I know, I know, no cameras allowed in the boiler room during construction. Safety thing, I understand. Same reason no ones ever filmed our apprentice doing HIS thing ::-) Only rumours.

    ME
  • Uni R_2
    Uni R_2 Member Posts: 589
    Where are the small cheap circs?

    So if there were smaller circs out there (for example 1/10th the GPMs of a 007) and any small zone could be be sized within say 50%, what possible advantage would zone valves have? They draw power but don't do anything to start the heat moving. The circ pumps while the zone valves all try to obstruct/herd the flow and then the actual flow of any zone is dependent on the other zones.

    The smallest circ that I've seen are Grundfos 15-10s, Taco 003s and the odd Laing. Sad part is a 15-10 without IFC coasts more than a 15-58IFC 3 speed -- if you can find an iron 15-10. Anyway, if smaller pumps than these priced similar to 007s were available, I wouldn't see any advantages to zone valves.
  • Ross_7
    Ross_7 Member Posts: 577
    Higher CV

    I usuall pick a ZV with a higher CV (like 7)with 1" sweat connections for DHW (less restrictive), & if your'e prioritizing, which you are,the pump on the system is already dedicating itself to the call for the indirect. I haven't had any issues to date. JMHO.
    Ross
  • hot_rod
    hot_rod Member Posts: 23,187
    What size is the boiler?

    A high Cv zone valve should easily move 75K or more. That seems to cover most of the size jobs you seem to do?

    hr
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • CC.Rob_4
    CC.Rob_4 Member Posts: 37
    been there!

    Several years ago, I literally came within inches of plopping a 5-yr old into a bathtub of ~160F water. Only thing that stopped me was the greater than normal steam coming off the water. Didn't seem right. Checked it with my fingers and was quickly scalded.

    A service tech had been checking zone valves that day and left the ZV on the indirect on manual open. Boiler was dumping into the indirect for about 6-7 hours.

    Just thinking about this sends shivers down my spine. Words cannot express how scary that was. We now have a circulator on the indirect (for performance) and a tempering valve (for safety) on the DHW output.