Make Up Air

ChasMan
Member Posts: 472
I got a quote on a boiler install that includes a Fan In A Can. I dont have enough cubic feet in my basement to support combustion. With a powered make up air unit like this, can I put a door on the boiler room and close it off? Also, are there any better units out there than a fan in a can? This is for an 80K 3 pass.
0
Comments
-
Fan in a Can
Yes, FIAC will allow you to close off the boiler room as many do. Tjernlund, Field and Exhausto all make systems in various types to suit you."If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0