Gravity Hot H20 Conversion
Bruce M
Member Posts: 166
Does the sytem work properly now? If it does, leave it alone. A properly piped gravity system is a work of art with few moving parts. It is hard to perfect upon perfection.
0
Comments
-
GRAVITY HOT H20 CONVERSION
HI ALL,
LOOKING AT CONVERTING AN OLD GRAVITY HOT H20 SYSTEM TO CIRCULATING H20.LOOKING FOR ADVICE ON MAYBE PRIMARY SECONDARY WITH CONDENSING BOILER.ANYONE DONE THIS?
THANKS........JK0 -
The
gravity system may work well but the heat source may be lacking in overall efficiency. From my experience in gravity conversions to a mod-con replacement is generally in the 30-50% reduction in fuel consumption.
$omething to consider...0 -
If the system is functioning under gravity, fueled by a gas conversion burner and the homeowner is fed up with high fuel bills than your only option is a mod-con boiler.
If TRVs (thermostatic radiator valves) are installed on the radiators at the time of conversion [highly recommended] then every room will be "zoned" with potential system efficiency maximized. The Vitodens by Viessmann is a natural choice for such a system and in most cases primary/secondary will not be required. Such a system is an ideal load for the Vitodens and its integral variable speed circulator.
If you don't use TRVs, primary/secondary will be required.
Properly sized and installed, the reduction in fuel consumption will be drastic regardless of the mod-con used with 50% being quite easy to beat.0 -
if it
is still gravity, the boiler probably is a 80 gallon capacity or more fuel sucking monster. Why pay to heat that water up before things get moving?
Go mod/con if gas, something like a 3 pass boiler if oil. Now you have a source to make and store hot water in an indirect tank. Convert to pumping. Maybe zoning? Look in the Library for tips on getting started.
0 -
I don't know mike,
I have a neighbor with a 3 story victorian, 1 zone, no TRV's.
house seems to heat fine.
I can easily see replacing that atmospheric boiler with any mod/con.
0 -
Gravity Conversion
TRVs aren't required but they are they offer the only way to maintain flow rates similar to what occurred via gravity. They also allow room-by-room zoning that self-compensates for solar and occupancy gains.
Without TRVs, 20+ gpm secondary (emitter) flow is common using the well suited circulators.
Any well-sized properly installed mod/con will do well driving the gravity conversion, but TRVs allow a directly connected mod-con to thrive.0 -
GRAVITY HOT H20 CONVERSION
Thanks for all the input!Iwill be doing my homework now..........JK0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements