Where to place air eliminator on a primary/secondary hydronic sy

I just installed a condensing gas boiler and added a caleffi load balencer . My question is where to put a spirotherm jr air eliminator ,On the primary side or secondary. The system is a mix of convection/radiant.

Comments

  • the answer could be

    as simple as, 'the primary side', but in consideration of asking the question at this point in the installation, you really should get a copy of dan's, 'hyrdonic radiant heating' so that you can stay on top, if not, ahead of the game
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,600
    Put it

    where the water is hottest, and if possible, at the lowest pressure.
    Retired and loving it.