What is the venting rate for Gordon #1 and #2?
Can anyone tell me the venting rate for these air valves? The Gorton site doesn't seem to list the specs.
Steve0 -
not sure if ....
this helps. a #1 is same as a Hoffman 75. a gorton #2 is 4- #1.0 -
Venting rate
With 3 oz of pressure in the system the venting rate is .7 CFM for the Gorton #1 and 2.2 CFM for the Gorton #2.0 -
Thanks. I'm surprised that Gorton doesn't display this information on their web site.0