Radiant & potable Same heater
I"mnot sure I understand what you are doing.
one joist bay has two runs of 5/8" pex, then you skip a bay, then another bay has two runs of 5/8"??
That's not a very good install. You don't need 5/8" for that and you'll have crazy heat stripes.
You need a heat exchanger as well. I'd use a variable speed injection controller for the water heater side pump.
Loops need balancing valves on them.
Hope that helps.
Hope that helps.
BTU and control circuit layuout
Looking for assistance in control device and circuit layout.
Subject:
1. existing 1/2 inch pex in 20 X 20 foot room.
2> adding TWO 20 X 20 rooms with double 5/8 inch pex
strung every other beam (bay).
3> New water heater 75,000 BTU A.O. Smith GAS fired Vertex
*** http://www.hotwater.com/products/residential/rg-vertex.html ***
has standard 3/4 inch potable out top and out of side for radiant heat.
4. Geographic locale: Long Island, N.Y.
Unit will provide house potable and three room radiant heat.
Concerned about overall BTU capacity and pump types
necessary to drive the two different pex diameters???
Also what would be preferred mixer/control devices?
Any ideas?0 -
Does the water heater have a seperate coil in it for space heating?
No seperate coil
just two sets of supply/return 3/4 inch feed lines.
try this link. The model number:GPHE50100
Manual:
http://www.hotwater.com/lit/im/media/res_gas/197423-001.pdf0 -
code?
does your local building code allow for combined space heating and domestic hot water?0 -
potable code
probably allows as long as pex and EVERYTHING in the circuit is rated potable, however I believe the pex is NOT so will probably opt for seperate tankless on-demand. Alternate would be to use a heat exchanger for the potable section. any pros or cons to either??0 -
heat load
what is the expected heat load for the 1,200 sq ft ?0 -
If the vertex will be there anyway, and has the output to meet DHW and heating, use the heat exchanger, it will do a better job for heating than the tankless.0 -
NRT.Rob, crazy heat
stripes for sure LOL :-)..
My oops in description, every other END joist in each bay was double drilled (1 1/4") to accept dual 5/8" pex running in each bay.
What brand/model variable speed
controller and balancing valves would you advise?
""Author: NRT.Rob
Hope that helps. ""
heat load
is actually THREE 200 square feet rooms, each with at least one exposed outside wall. all three are well insulated. Two will have newly installed 5/8" pex and one has pre-existing 1/2" pex.0 -
I'd just use 1/2" pipe two per bay, connected to a manifold with flow meters/balancing valves, and loop the rooms individually so I can balance/zone them.
I like a tekmar 356 injection mixing controller for this kind of a setup (two pumps and a heat exchanger). If you are willing to run "bang bang" and your water temps aren't too high, then you might skip it too, but it's a nice addition.0 -
how
did you attach the 5/8 pex to the floor?0 -
Are you using plates or just staple up?0 -
Pex fastening
is by stapled up aluminum plates.0 -
Why 5/8 inch PEX
Because the very old and very thick double floors in this very old building provide a deterrent to heat. The double
5/8 inch was thought to provide more "horsepower" (higher
flow/BTU throughput). Before you ask, NO!, the antique custom floors could not be disturbed in order to lay the radiant pex on the top side.
The layout is attached. Dual 5/8 pex running through EACH bay.0 -
Tankless -vs- Vertex Condensing
The tankless was only for the domestic potable, since the whole system is not potable certified. Also if one unit fails you dont lose both functions (heat AND hot water)
Also, doesn't a heat exchanger cost almost as much as a small tankless?0 -
It does, but the vertex will do a better job of both heating and hot water, and if it's there, you should use it for both.
the "whole system" only has to be potable up to the heat exchanger.0 -
5/8 will not help your output and that's about the most difficult possible way to install a joist heating system ever.
3/8 or 1/2 pipe, all penetrations on one end, using the "pull method". down and back through the penetrations, then pull from that up the joist bays with a loop of tubing.0
- 87.4K THE MAIN WALL