ground source heat pump heat exchanger plugging with sediment.
dnr
Member Posts: 3
I am working on a ground source water to water system that has a plate type heat exchanger(command aire).The load side of the HE plugs up and locks out on high head.flush it out and it is good for a year or so. I have put treatment in the water but doesnt seem to help.any ideas?
0
Comments
-
Water?
Is this a closed loop or open loop system? If it is open loop, then minerals or iron bacteria could be the cause and are next to impossible to treat or filter. If it is a closed loop system, I would look to the components as the source of contamination.0 -
this on the closed loop side...
correct? If so either the system has trapped a mass of particulate which is not carrying through on to your flush point, but is perfectly happy to go to your HX in suspension. Put a prefilter in front of the HX and see what happens. Plate HX are kind of a pain to clean in my experience. Otherwise, If the system is clean and there is no debris in the lines, you have to be "galling or eroding" some material in the piping which is moving to the HX. What is the material?0 -
It is closed loop, load side. Not sure what the particles are, they are small grey pieces. we have flushed the system, but after time they plug HE.0 -
Are the small grey pieces hard like plastic? Any chance of a disintegrating dip tube in a buffer tank?
What type of tubing?0 -
Type of Water Left in the System
When the system is being flushed, are you using house tap water to flush it with or is it a recirculating pump tank system? Is this domestic house water --- the water that is left in the system or do you drain this out and add a distilled source of water? It could be the minerals coming out of suspension with heat and causing flow problems with the fine passage ways of the plate exchanger. Water chemistry is worth a check..0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements