Monoflo branch legnth
![[Deleted User]](https://secure.gravatar.com/avatar/4b9867bef9a49163e8895d646f6d6f08/?default=https%3A%2F%2Fvanillicon.com%2Fe99a77efb57c283fc93dd671c276ca6b_200.png&rating=g&size=200)
[Deleted User]
Posts: 15
reasonable distance we can expect a branch on a 1x1 x 1/2 monoflo system to be effective?
Thanks!
Thanks!
0
Comments
-
It depends
on pressure drops and required flow rates. Take a look at The B&G Handbook from the Libary and scroll to the section on Monoflo tees.Retired and loving it.0 -
Thanks Dan ... thats exactly the 'push in the right direction' I was looking for.
0 -
Thanks Dan ... thats exactly the 'push in the right direction' I was looking for.
0
This discussion has been closed.