pressuretrol setting
Dan C._4
Member Posts: 70
Depends on what kind of pressuretrol it is. If it is the one the comes with the IN5 now then main should be 1 1/2 and diff should be 1. The main is the cut out. The cut in is the main minus the diff.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=329&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=329&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
pressuretrol setting
Hi ALL
What is the the correct pressuretrol setting on a Burnham IN5 steam boiler for a one pipe system?
is it Main 1 and differential 2?
1 1/2 and 1/2.
which one is cut in and which one is cut out.
meaning is differential cut out or is differential cut in?
Thanks
0