pressuretrol setting

Dan C._4
Dan C._4 Member Posts: 70
Depends on what kind of pressuretrol it is. If it is the one the comes with the IN5 now then main should be 1 1/2 and diff should be 1. The main is the cut out. The cut in is the main minus the diff.

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=329&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • Rena Nicholson
    Rena Nicholson Member Posts: 20
    pressuretrol setting

    Hi ALL
    What is the the correct pressuretrol setting on a Burnham IN5 steam boiler for a one pipe system?

    is it Main 1 and differential 2?
    1 1/2 and 1/2.

    which one is cut in and which one is cut out.
    meaning is differential cut out or is differential cut in?

    Thanks