Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
pressuretrol setting

Dan C._4
Member Posts: 70
Depends on what kind of pressuretrol it is. If it is the one the comes with the IN5 now then main should be 1 1/2 and diff should be 1. The main is the cut out. The cut in is the main minus the diff.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=329&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=329&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
pressuretrol setting
Hi ALL
What is the the correct pressuretrol setting on a Burnham IN5 steam boiler for a one pipe system?
is it Main 1 and differential 2?
1 1/2 and 1/2.
which one is cut in and which one is cut out.
meaning is differential cut out or is differential cut in?
Thanks
0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements