Are these boilers leaking?

I used an old b&w camera and connected it to our security system. I’ve used a webcam with a old laptop to catch other problems. It’s very helpful in situations where you’d have to stand around for hours watching and waiting.

Thanks.

Comments

  • BobAuerbach
    BobAuerbach Member Posts: 4


    I'm looking for some expert advice and was told The Wall is the place to go. My company purchased two Peerless TC-12's last year, which now have a white crust on most of the lower port connections. We had a lab test it and the result was predominantly Sodium Carbonate. The water is treated with a softener, ph is 7.8 and very little makeup is used. The contractors looked at them and said that the boilers are leaching something and not leaking. My 25-year experience tells me they're leaking. I appreciate any professional advice and thanks in advance.
  • Bruce Stevens_2
    Bruce Stevens_2 Member Posts: 82
    Symantics

    to leach means to carry a soluble mineral via the transporting agent water.
  • DJ_5
    DJ_5 Member Posts: 4
    Condensing?

    I am no expert, but does the unit sweat? It may not even need to sweat alot, but if they keep the salt pellets or laundry detergent nearby and it is pulled into the burner and then condensed it would cause sodium carbonate deposits. But the boiler would not need to rain too much to cause this so it may be difficult to pinpoint. Let me know if I am up in the night here, not that I have to ask that, but its my 2 cents
  • Bruce Stevens_2
    Bruce Stevens_2 Member Posts: 82
    The first picture looks like leaking flue gaes

    but the second looks to be aronud the push nipples, I am assuming the sample was from the second location?
  • Phil_17
    Phil_17 Member Posts: 178
    leaking boilers

    testing of the water inside the boiler and the deposits outside the boiler could establish whether they are chemically related and therefore how could that be if there were no leaks?
    i suppose you could do a hydro test [was one ever done-many people skip this step] when warm weather comes and see any leaks that way.
    nbc
  • BobAuerbach
    BobAuerbach Member Posts: 4
    Leaching Boilers

    One of the boilers has evidence of condensation at the breeching connection and no chemicals are stored in there.

    The first picture shows the leaking exhaust and white substance. Those 6 clean-out plates were originally installed too high and have been reinstalled properly. The samples were taken from the lower ports (both sides of each boiler) where the graphite gaskets are.

    The test results of the water samples have not come in yet.

    About a week after samples were scraped from the boiler, I noticed a re-growth of the white substance. I cleaned the area and set up a time-lapse camera. Two days later the camera caught what I believe to be a leak. It will only last about five minutes and then crust over. After a week of capturing video, it can be predictably seen when the boiler is alternated daily with the other and about ten minutes after start up. The following link is a one-minute video of a twenty-minute time frame, left is up.

    Video Link

    I really suspect the draw rods and lack of swing joints on the headers.

    Thanks again.
  • Bruce Stevens_2
    Bruce Stevens_2 Member Posts: 82
    Draw Rods maybe

    but I would suspect no swing joints as my first guess, as the boiler heats up it may still weep but not noticably as it would evasporate as fast as it weeps
  • Boilerpro_5
    Boilerpro_5 Member Posts: 407
    As soon as I saw the piping.....

    I figured they are leaking. I have seen this before....welded header on cast iron boiler = leaks between sections.

    Boilerpro

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Al Corelli_2
    Al Corelli_2 Member Posts: 395

    There was an error rendering this rich post.

  • kpc_12
    kpc_12 Member Posts: 24
    bingo...

    no swing joints...kpc
  • seabee570
    seabee570 Member Posts: 89
    boilers

    I assume these are hot water boilers? How do you know that very little make-up is used? Is the make-up metered? Why are you using soft make-up water?(if these are hot water boilers?)I would check with peerless about use of soft water for make-up and see if it is in recommended range?The ph does not seem bad,but soft water into hot water boilers is not recommended.
  • yeap, that'll do it..

    Without any swing joints as others mentioned, the boiler sections will "spread" and moan for more expanison within movement. I've seen boiler section "ears" ( where boiler rods connected to) cracked several places due to this piping set up.
  • Timco
    Timco Member Posts: 3,040


    Is there any reference to swing joints in 'Lost Art'? I have a peerless that is hissing and next week will be checking for a leak. Condensate appears on the mains coming out of the jacket, then hisses, but stops hissing and the condensate disappears when steam begins.

    Tim
    Just a guy running some pipes.
  • yes, swing joints

    i've looked also and can't find a good reference/pictures anywhere
  • Swing joints in LAOSH,

    Dan mentions them on pg. 52 & 53. He doesn`t go into swing joint construction, but you`ll get the idea.


  • With the tight space for piping this looks to have been a perfect application to install swing joints in to a “drop header”.
  • Al Corelli_2
    Al Corelli_2 Member Posts: 395
    Time Lapse!!!

    Absolutely one of the coolest ideas ever!

    I watched that three times. My wife thinks I'm crazy.

    Outstanding Ingenuity.

    How did yoou do it?
    What equipment did you use?

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"

    There was an error rendering this rich post.

  • the time lapse

    sure makes it look like a leak, dark 'line', to me, with evaporation, to white, following
  • BobAuerbach
    BobAuerbach Member Posts: 4
    System Info

    These are steam boilers with duel fuel (gas/oil) modulating Power Flame burners running at 2 psi. and connected to a drop header. It is a vacuum system from the 20’s that heats half a square block of various sized office buildings. The total EDR of the entire complex is approximately 8,542 S.F. The F&T’s are blown out monthly and a trap maintenance program in place. The make-up is not metered but it takes about 6 weeks (with blow-downs) before it requires any. All of the buried mains have been dug up and sleeved. All in all the system runs fairly well with no major problems.

    Thanks.
  • That's not a leak...

    ...according to Propress.

    Time-lapse video....well done, sir!