Oversized steam boiler

R. Kinkopf
Member Posts: 3
I was called to trouble shoot a mouat steam system. The boiler was cycling on the pressure control set at 2 oz because if it was set higher they were blowing steam through the condensate pump. The system is vented throught the condensate pump which was wired to be activated by a mcm pump control on the boiler. Water, if needed was introduced into the condensate receiver tank.
All of the original vents were in place, but steam was blowing through the vents.
I c ouldn't figure out why the steam would be blowing through the vents a 2 oz of pressure. I finally surveyed the connected radiation and found that the boiler was twice as big as needed.
Question #1 Is the steam blowing through the traps because of the oversized boiler?
Question #2 What can be done to correct the situation short of replacing the boiler?
I did not install the boiler. As a heating steam heating contractor, I was asked to help out a friend.
What do you think????
All of the original vents were in place, but steam was blowing through the vents.
I c ouldn't figure out why the steam would be blowing through the vents a 2 oz of pressure. I finally surveyed the connected radiation and found that the boiler was twice as big as needed.
Question #1 Is the steam blowing through the traps because of the oversized boiler?
Question #2 What can be done to correct the situation short of replacing the boiler?
I did not install the boiler. As a heating steam heating contractor, I was asked to help out a friend.
What do you think????
0
Comments
-
Oversized boiler
I was called to trouble shoot a mouat steam system. The boiler was cycling on the pressure control set at 2 oz because if it was set higher they were blowing steam through the condensate pump. The system is vented throught the condensate pump which was wired to be activated by a mcm pump control on the boiler. Water, if needed was introduced into the condensate receiver tank.
All of the original vents were in place, but steam was blowing through the vents.
I c ouldn't figure out why the steam would be blowing through the vents a 2 oz of pressure. I finally surveyed the connected radiation and found that the boiler was twice as big as needed.
Question #1 Is the steam blowing through the traps because of the oversized boiler?
Question #2 What can be done to correct the situation short of replacing the boiler?
I did not install the boiler. As a heating steam heating contractor, I was asked to help out a friend.
What do you think????0 -
Oversized boiler
I was called to trouble shoot a mouat steam system. The boiler was cycling on the pressure control set at 2 oz because if it was set higher they were blowing steam through the condensate pump. The system is vented throught the condensate pump which was wired to be activated by a mcm pump control on the boiler. Water, if needed was introduced into the condensate receiver tank.
All of the original vents were in place, but steam was blowing through the vents.
I c ouldn't figure out why the steam would be blowing through the vents a 2 oz of pressure. I finally surveyed the connected radiation and found that the boiler was twice as big as needed.
Question #1 Is the steam blowing through the traps because of the oversized boiler?
Question #2 What can be done to correct the situation short of replacing the boiler?
I did not install the boiler. As a heating steam heating contractor, I was asked to help out a friend.
What do you think????0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements